EIFS RAINSCREEN
EXTERIOR or SIMPLY STUCCO THREAD
Subject: EIFS
Rainscreen Exterior or Simply Stucco
Richard, Nina, Rik,
Ned Jeff, Timothy, Mark, David B., Jeffrey, David A., and Wagdy:
We are hoping to
join your BEC group here shortly with a BEC - Minnesota (Our state AIA
is the organizing AIA group over the local city chapters here.) I am in
the process of organizing it now with AIA Minnesota.
Coincidentally, I
have an exterior building envelope question that has arisen in the past
few weeks that is right up the alley for the BEC Councils. Could I
politely request your opinions on the question? And can you respond
immediately since we have a meeting this afternoon to make a decision on
the issue? Thank you very much.
The Owner,
Architect, Contractor, and various consultants on the project in
question are wrestling with the choice of using either EIFS (with the
most current rainscreen drainage features) or straight stucco as an
exterior finish on a large hospital addition. The existing hospital has
both stucco and EIFS, and there have been leakage problems with both
systems. Most of the leakage problems were due to flawed flashings at
window penetrations and joints. However, the General Contractor and the
consultants (including myself) are very leery of using EIFS because of
the historical failures associated with it and its thin, relatively
vulnerable veneer. Another negative factor associated with the EIFS
systems is that insurance companies are pressuring both the Contractor
and many architects to avoid using EIFS because of it failure record and
litigation risk.
The Architect
insists that the most current rainscreen type of EIFS has addressed its
previous causes of failure, and is a viable system. They would like to
use it.
The system will be
fastened to 6² steel stud wall framing, with the insulation applied to
the exterior.
Finally, besides
which system do you recommend, what do you see as the respective layers
of material from the studs outward? Where and what is the vapor
barrier? How many layers of sheathing would you use, how thick, and in
what order?
The Architect is
contemplating using 2' of rigid insulation.
Thank you for any
input you may have about this.
I look forward to
sharing recommendations about building exteriors in the future through
BEC.
Judd Peterson, AIA
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
Judd; Glad to
hear about the Minnesota BEC. We could use more representation from
cold climates.
Regarding EIFS or
stucco, I would pick the stucco with a significant caveat. It is
possible to use the stucco as part of a drained cavity system, assembly
as follows:
-
Cold formed
steel stud framing with no insulation in the stud space.
-
Exterior
sheathing, probably Dens Glass
-
A continuous
air and vapor barrier membrane, by Grace or Henry for example.
-
Vertical galv
steel zee furring with all of the fasteners sealed.
It may help to
space away from the wall 1/4 inch for drainage and a better thermal
break. The depth should be around 1/2 inch larger than the thickness of
the insulation to provide an continuous drainage plane.
-
Semi rigid
mineral wool insulation, thickness to comply with energy code or
ASHRAE 90.1.
-
Paper backed
self-furring metal lath. The paper does not provide weather
resistance but keeps the stucco from going through the lath into the
air space.
-
7/8 inch three
coat stucco with plenty of control joints.
-
Stainless
steel flashing to drain the cavity.
After all of that,
I would then change the stucco layer to Alucobond dryjoint metal panels
anyway. Linda Brock has a book that shows the stucco system in some
detail. I can find the title if you need it.
Regarding the EIFS,
assuming that the drained systems do fix the weathering problems (i am
not totally convinced), you still end up with a building that
relies extensively
on sealant for performance but the sealant cannot be reasonably
maintained over the life of the building. In 15 or 20 years when the
sealants need to be redone the building will need to have a network of
silicone "band aids" applied to the face of each sealant joint because
it is impossible to remove the old sealant without damaging the EIFS.
Despite what Dow says, the silicone strips are ugly. I don't think it
is prudent to select a system for a significant institutional project
that cannot be reasonably maintained for the life of the building and is
so easy to damage.
I'm interested to
here other opinions form you guys.
Dave
Subject: RE:
EIFS Rainscreen Exterior or Simply Stucco
While I agree for
the most part with David's comments, I shall offer a few of my own
thoughts:
* Insulation in
the cavity should be evaluated through a computer simulation tool for
due point and thermal performance.
* The exterior
sheathing is not as critical with the installation of a water membrane,
but when we tested that product it performed only slightly better than
paper-faced gypsum sheathings before delamination. There are several
cement-based sheathings available as well as other non-paper faced
gypsum panels which work much better!
* The use of a
breathable air/water barrier may work better here moving the Vapor
barrier further interior in cold climates if additional insulation is
required. If the 2" rigid is acceptable then David’s assembly is great.
* I am not a fan
of conventional (7/8" 3-coat exterior) Stucco in cold climates! Too many
cracks.
Later
Rik Master, AIA
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
Rik; Good points.
All of these are trade offs and sometimes personal preferences. Many
qualified architects can come to different solutions.
* I agree that it
may be possible to place batt insulation within the stud spaces if
proven acceptable by computer modeling. However, if more than around
50% of the total R value is in the stud space, then the vapor barrier
may need to be located on the interior face and the air barrier may need
to be vapor permeable. I would rather keep all of the insulation in the
air cavity which also provides for an open and continuous surface of the
sheathing for installation of a combined air and vapor barrier membrane.
* I agree that
there are several cement-based sheathing products that would be
excellent choices. The reason I don't like paper faced products is not
there performance once covered, but the problems that might arise from
being exposed to rain and snow during construction.
* See the first
comment about the batt insulation and air/vapor barrier. I would bet
that actual heat loss throught the opaque portions of the wall is a
relatively minor percentage. I would much rather have a system that has
a higher probability of long-term performance regarding the control of
air, vapor and water over one that has a higher R value.
* Agree with the
last comment wholeheartedly, try those metal panels instead.
Dave
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
To All:
Thank you all so
much for responding to my questions so thoughtfully. This is everything
that I¹ve thought that BEC should beŠa resource for great advice on
exterior envelopes.
As for my own
opinion on this, I am in agreement with the rest of you here. I see that
most of us are preferring true stucco, assembled with the ability to
drain and weep, with subflashing membranes that act as vapor barriers /
weather barriers simultaneously, and plenty of expansion joints.
A couple of other
things I recommend: I actually prefer using the EIFS acrylic finish
coat on my 7/8² stucco because it seems to hold together against those
hairline cracks better with its flexibility. If you really want to seal
off the water penetration on the face of either stucco or EIFS or
exposed concrete, consider using Sika 550W elastomeric coating. It’s
super flexible, even in extreme cold, can span cracks, and comes in over
240 standard colors. It sheds water and still breathes vapor. The
downside is that the color becomes very uniform and it has the slightest
rubbery sheen to it when you¹re looking at it within a few feet of
distance. That may dull with age. We¹ve used it on several buildings
with exposed concrete frames, which we coated, and the results are very
nice. Really cleans up the buildings. Protects rebar in the exposed
concrete too. It’s a little expensive, but very effective.
Getting back to
the stucco vs EIFS situation, our group here in Mpls got a little hung
up on whether there should be Z clip furring to carry the stucco beyond
the rigid insulation. I think the consensus here was that it would be
fastened and sealed against the vapor barriered sheathing, between the
insulation boards. The sheathing would act as a thermal break. So I
guess we agree again with Dave here.
Then there was a
discussion about whether the stucco would need another sheathing layer.
I like the paper-backed wire mesh which eliminates that thickness.
Finally, my first
choice for exterior materials here was metal panel cladding, like
Alucobond, so again, we seem to be in agreement. That choice was
eliminated for budget, unfortunately.
Regarding the
possibility of trading advice in the future, we might consider
developing a ³List-serve² function on the internet. I don¹t know if any
of you belong to a list on the internet, but it allows you to
voluntarily subscribe to a single location which ties you to the entire
list of subscribers with a similar interest. You can ask questions of
the list (of all subscribers), and they go out to everyone¹s email
address on the list. Those other subscribers can either simply read the
info, or reply with comments or answers. The replies go out to everyone
on the list. You get threads of topics, some of interest to you and
some not. You reply, save, delete the emails as you see fit.
(Personally, I
belong to the Fiddle-L list where, for years, I’ve asked fiddling
technique, theory, style, general info questions, and have gotten
responses and advice from knowledgeable, great fiddlers from all over
the world. Occasionally, there are the personality and topical taste
clashes, but in general, it¹s a valuable connection.)
Judd Peterson, AIA
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
To all:
Great
conversation. Since as architects I think we are still graphically
inclined, I took the liberty to sketch what I understood to be the
direction of the conversation and have attached it.
One additional
question for all regarding the assembly: In David’s initial description
he noted to provide stainless steel flashing to drain cavity. I concur
that stainless is appropriate but I¹m equally concerned that there is a
significant potential for the galvanized zee furring to rust and stain
the stucco. Undoubtedly, the zee furring will be field cut and
scratched compromising the galvanized coating. Does this concern anyone
else?
Regards,
Ned S. Kirschbaum, AIA, CSI, CCCA, LEED AP
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
Yes, that it might
rust and that the staining will migrate down and out on the flashing
more than through the stucco.
Rusting of the
lath could also occur if too much moisture and free water is in the air
cavity. This has more potential to migrate through conventional stucco
in my findings since it is already in that layer and travel the hairline
cracks common in this material.
Rust, water, air,
etc. take the easiest path of resistance.
PS I agree! We
need a Forum for this kind of GREAT discussion! We are looking into
various options for BEC Chicago, since we get into the same kind of
discussions. So would love any suggestions!
Later
Rik Master, AIA
Subject: Re: EIFS
Rainscreen Exterior or Simply Stucco
Hi everyone,
again!
One, hopefully
last, question. I was thinking of using pressure-treated wood furring to
get the drainage cavity behind the stucco. Any comments on that?
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
Richard,
At MnSCU
(Minnesota State Colleges and Universities), we have found, over the
hundreds of buildings that they¹ve reroofed, that pressure-treated
lumber has a tendency to warp after installation, even if kept dry.
Early on, MnSCU believed that they were being conservative by installing
pressure-treated lumber for parapet blocking and cant construction
around the roofing. What they found was that the lumber warped so much
that it was tearing up the sheet metal flashings and roof base
flashings. Since the lumber was being covered by subflashing membranes
and sheet metal, they decided that the lumber was intended to be dry and
that they would not use pressure-treated lumber, just plain, oven-dried
lumber. They haven¹t had any problems since.
I only use
pressure treated for decking or sleepers where I can’t avoid moisture
and the materials are expected to be replaced in the relatively short
term.
How about using
something like Korolath PVC shims to space the stucco lath off the
sheathing, except with some continuous length? Maybe something like PVC
piping ripped in half?
Judd Peterson,
AIA
Subject: RE: EIFS
Rainscreen Exterior or Simply Stucco
There may need to
be some disclaimer that these are individual opinions without benefit of
full knowledge of the project and cannot be used as professional advice
nor do they represent the views of BETEC or NIBS, otherwise, I think it
would be great. Maybe we all have some other topics to cover (such as;
success getting the window and curtainwall manufacturers to allow
flashing the air barrier into their glazing pocket, how to get a double
seal to storefront sections, how to integrate a hollow metal door frame
into a drained cavity wall, how to deal with very low allowable
accessible operating forces on doors while still keeping them closed
against the wind, etc. etc.)
Regarding
Richard's last suggestion, we have been avoiding PT wood because we
worry it will warp over time in a wet environment that goes through
significant temperature swings, no basis in history for that assumption
though. Anyone with actual project experiences?
Dave |